You could have had a brown out or brief power outage. If so, there is a thermal overload deep inside compressor that probably tripped. It opens on high internal temperature of compressor. Compressor will not run untill the compressor cools a bit, almost to ambient temp. Thermal overload will reset and compressor will start and run.
Could 1 to 3 hours to reset.
This is common in extreme grid loads. Hope that was all that happened. Good luck
And you are the winner! Thank you very much. I knew that brief power outage had something to do with it. It just needed to cool off and I'm blowing cold air again. Thanks again.
Lotta newer units have a 5-min timeout timer in the control board. It helps protect the compressor from short-cycling.
If these power or cycle off for any reason, it waits 5 min before allowing compressor to restart. Maybe your power flickered and caused a timer cycle?